Hello all,
I'm hoping someone can help me with this. I have a Gateway Timer script that runs at a fixed rate (every 500 ms). The idea is that it is a heartbeat monitor so every 500 ms, it should read a new value from the PLC (Heartbeat_from_PLC), compare it to a previously saved value (Prev_Heartbeat) and if the value is unchanged, it indicates some sort of communication error and it will set a tag (Heartbeat_Alarm_Flag) that will alarm after 10 s and the alarm then triggers another tag (PLC_Comm_Err) to turn on. After that, it saves Heartbeat_from_PLC to Prev_Heartbeat and then sets a different heartbeat value, which is sent to the PLC and used only by the PLC (Heartbeat_to_PLC).
The code works fine except for one thing - after the 10 s alarm, it takes around 25 s for the PLC_Comm_Err tag to turn on and I cannot figure out why! The Gateway Timer script is below:
def handleTimerEvent():
#===-HEARTBEAT ALARM====#
# Read current values
Heartbeat = system.tag.readBlocking(['[MTCE]Heartbeat_from_PLC'])[0].value
Prev_Heartbeat = system.tag.readBlocking(['[MTCE]Prev_Heartbeat'])[0].value
# Compare current Heartbeat value to previous value
if Heartbeat <> Prev_Heartbeat:
# Reset the alarm flag
system.tag.writeBlocking(['[MTCE]Heartbeat_Alarm_Flag'], 0)
else:
# Set the alarm flag (alarm flag has 15 s alarm delay)
system.tag.writeBlocking(['[MTCE]Heartbeat_Alarm_Flag'], 1)
# Set the PLC_Comm_Err if heartbeat alarm flag has been on for 10 s
if system.tag.readBlocking(['[MTCE]Heartbeat_Alarm_Flag/Alarms/Timer.IsActive'])[0].value == 1:
system.tag.writeBlocking(['[MTCE]PLC_Comm_Err'], 1)
else:
system.tag.writeBlocking(['[MTCE]PLC_Comm_Err'], 0)
# Save the heartbeat value to the Prev_Heartbeat variable
system.tag.writeBlocking(['[MTCE]Prev_Heartbeat'], Heartbeat)
# Check if heartbeat value sent to PLC should be reset
if Heartbeat > 99:
# Reset heartbeat counter
system.tag.writeBlocking(['[MTCE]Heartbeat_to_PLC'], 0)
else:
# Set new value
system.tag.writeBlocking(['[MTCE]Heartbeat_to_PLC'], Heartbeat + 1)
Some things to note:
-
The PLC increases the value of Heartbeat_from_PLC as long as it gets a new value of Heartbeat_to_PLC from Ignition.
-
Heartbeat_Alarm_Flag alarm settings are shown below:
If anyone could shed light on why turning on PLC_Comm_Err takes so much more than 10 s after Heartbeat_Alarm_Flag turns on, I'd be very grateful!
Thanks!