UDT Expression Tag Alarm With Active and Clear Delay Prevents Pipeline From Triggering
Hi
I'm working on a Heat Stress system that uses tag alarms and pipelines to notify users when the conditions of their work area requires additional relief from work.
Inside a UDT, I have it setup where, given a temperature memory tag (will be an OPC tag in Production), an expression tag will take the value and translate it into a state integer (ex temp > 31.5 state = 5). I have 4 alarms setup for the expression tag, when the state (value) is 2, 3, 4, and 5. Each of the 4 alarms has an active and clear pipeline notification that is used for contacting users. Everything is working properly up to this point.
However, I want to prevent notification from occuring when the state is constantly switching between 2 because of the temperature reading being on the cusp of the state thresholds. I attempted to use the Active Delay and Clear Delay with a delay of 30 seconds for each to accomplish this. It appears though that when I implement these delays that it prevents the alarm pipelines from triggering altogether.
Is this the correct path I should be taking to implement the delays?
No, you should be using deadband on the temperature value, not time delays.
It is somewhat difficult to do with your architecture, where you are turning off lower-priority alarms when higher levels are hit. Consider not using an expression to yield a state. Instead, place the four alarms on the temperature tag with the levels as the alarm setpoint, and include a small deadband on each alarm. Let the lower priority alarms stay active when the higher priority engages.
The reasoning for the expression tags was because we have a different set of relief states for workers who are acclimatized vs non-acclimatized to the conditions of the work area. I guess I could still manage to have that work out as alarms directly on the temperature tag. In my mind it just seemed simpler the way I initially set it up.