UDT Expression Tag Using OPC Tag Path Error
I am trying to use a UDT to read several Modbus registers, perform a calculation and return a value. Please see code below. Returns a “Error_Configurtion“ message. I feel it is simple or I just don’t have the correct Expression for the tag path to the OPC device.ModbusRegister. Any suggestions?
// Current Unbalance Formula
// Calculate Absolute Maximum Deviation of Phase Currents
(max(abs([{deviceName}]{unitId}.HRUS577 - [{deviceName}]{unitId}.HRUS580),
abs([{deviceName}]{unitId}.HRUS578 - [{deviceName}]{unitId}.HRUS580),
abs([{deviceName}]{unitId}.HRUS579 - [{deviceName}]{unitId}.HRUS580))
// Divide by Current Average Magnitude * 100 for %
)*100
You aren't actually referencing the tags. This is the one rare case where the usage of tag() in an expression is allowable. You'll need to rebuild how you construct the dynamic paths to be strings, and place them each inside of tag().
Edit: seems like everyone's reading comprehension is off, or I need more coffee. You cannot do what you are trying in an expression tag.
But how does the tag() expression handle OPC UA Server paths? For this instance of my UDT, I have set up 4x unique parameters to use as a template. The deviceName references the Modbus TCP device on the gateway and the unitId references the Modbus ID.
No, this is not a task for tag().
Make actual member tags in the UDT of type OPC with those parameterized OPC Item Paths.
Then the expression can reference them as {[.]SomeTag}.
Yup, I realized that after posting, I saw them as other tags in ignition when I first read through.
Still returning “Error_Configuration”
(max(abs({[.]CurrA} - {[.]CurrAvg},
abs({[.]CurrB} - {[.]CurrAvg}),
abs({[.]CurrC} - {[.]CurrAvg}))
{[.]CurrAvg}
)*100
Please post code as preformatted text, it preserves whitespace and syntax highlighting, see Wiki - how to post code on this forum. You can edit your post by clicking the pencil icon in the bottom right.
To me it looks like your first abs is missing its ending enclosing paranthesis (adjusted for better readability):
(max(
	abs({[.]CurrA} - {[.]CurrAvg}),
) / {[.]CurrAvg}) * 100
Ugh, those darn close parenthesis!!!
Here is what worked. Thanks @ryan.white & @pturmel !!!!!
(max(abs({[.]CurrA} - {[.]CurrAvg}),
{[.]CurrAvg}
)*100
You have excess parenthesis, two pairs of which can be eliminated.
max(
) / {[.]CurrAvg} * 100
I recommend indenting consistently so that the closing bracket lines up vertically with the function that opens the parenthesis (if both aren't on the same line). Add spaces both sides of mathematical operators. They're separate words and legibility is improved.
Make it easy for the next guy!
@Transistor,
I don't recall how Ignition handles math, but the * 100 needs to occur last in the calculation. This is why I had multiple parenthesis. You edits do look more clean though.
No, multiplication and division are commutative.
commutative
/kəˈmjuːtətɪv,ˈkɒmjʊtətɪv/
adjective
Mathematics
involving the condition that a group of quantities connected by operators gives the same result whatever the order of the quantities involved, e.g. a × b = b × a.
You can try it out in the expression editor.
The only caution I can think of is when restricted to integer maths better accuracy can usually be obtained by multiplying first and then dividing. This sequence avoids multiplication of the rounding errors.