Unable to connect to S7 1500 using OPC UA
Hi, I'm trying to connected an S71511 CPU to our ignition server using OPC UA (PLC is the server and ignition is the client).
I can do this no problem when I untick the certificate security on the ignition OPC UA configuration for the connection but when I tick the box I get the following fault message....
UaException: status=Bad_SecurityChecksFailed, message=sun.security.provider.certpath.SunCertPathBuilderException: unable to find valid certification path to requested target
at org.eclipse.milo.opcua.stack.core.util.validation.CertificateValidationUtil.buildCertPath(CertificateValidationUtil.java:413)
at org.eclipse.milo.opcua.stack.core.util.validation.CertificateValidationUtil.buildTrustedCertPath(CertificateValidationUtil.java:120)
at org.eclipse.milo.opcua.stack.client.security.DefaultClientCertificateValidator.validateCertificateChain(DefaultClientCertificateValidator.java:64)
at org.eclipse.milo.opcua.stack.client.transport.uasc.UascClientMessageHandler.onOpenSecureChannel(UascClientMessageHandler.java:469)
at org.eclipse.milo.opcua.stack.client.transport.uasc.UascClientMessageHandler.decodeMessage(UascClientMessageHandler.java:394)
at org.eclipse.milo.opcua.stack.client.transport.uasc.UascClientMessageHandler.decode(UascClientMessageHandler.java:382)
at io.netty.handler.codec.ByteToMessageCodec$1.decode(ByteToMessageCodec.java:42)
at io.netty.handler.codec.ByteToMessageDecoder.decodeRemovalReentryProtection(ByteToMessageDecoder.java:510)
at io.netty.handler.codec.ByteToMessageDecoder.callDecode(ByteToMessageDecoder.java:449)
at io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:279)
at io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:379)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:365)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:357)
at org.eclipse.milo.opcua.stack.client.transport.uasc.UascClientAcknowledgeHandler.decode(UascClientAcknowledgeHandler.java:171)
at io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1410)
at io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:919)
at io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:166)
at io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:722)
at io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:658)
at io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:584)
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:496)
at io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:995)
at io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
Caused by: sun.security.provider.certpath.SunCertPathBuilderException: unable to find valid certification path to requested target
at java.base/sun.security.provider.certpath.SunCertPathBuilder.build(Unknown Source)
at java.base/sun.security.provider.certpath.SunCertPathBuilder.engineBuild(Unknown Source)
at java.base/java.security.cert.CertPathBuilder.build(Unknown Source)
at org.eclipse.milo.opcua.stack.core.util.validation.CertificateValidationUtil.buildCertPath(CertificateValidationUtil.java:411)
... 34 more
8.1.27 (b2023042509)
Azul Systems, Inc. 11.0.18
On the back of this the certificate keeps getting quarantined.
Can anyone help with this please?
Can you upload the server certificate here so I can take a look at it?
Hi Kevin,
3ab86785b545b416200ebc897ca1f4ca9f41ccd9 [CN%3DPLC-1%2FOPCUA-1-10].der (1.1 KB)
this is downloaded directly from the ignition gateway
This certificate has an issuer that you also need to tell Ignition to trust.
O=Siemens,C=DE,CN=Siemens TIA Project - SandboxSA
Hi Kevin,
Thanks again for your help with this
I'm not sure how to do this, would this be an additional certificate?
Shaun
Yes, it’s another certificate you have to get from the PLC or TIA Portal somehow. Not sure exactly where it is configured.
Thank you, I'll take a look and let you know how I get on
Problem solved!
The certificate is a CA certificate which authorises the OPC certificate. The OPC certificate is automatically sent to the ignition server on connection but the CA certificate needs to be exported from the TIA project and imported to the Ignition gateway using the upload function.
Thanks for your help diagnosing this issue.