Hi all, thanks in advance for any help.
I received cleared notifications for voltage sag events that lasted less than 60ms. I did not receive an active notification for this event. The alarm configurations are using a 5 second on/off delays so an alarm should have never been generated. I also have no history of the event in either the alarm journal or the tag history. The device that triggered the event is SEL 735 meter using a DNP3 connection.
There were four events total, at two different sites. Phase A events lasted ~60ms while Phase B events lasted ~35ms. All look the same so I will post the images of one event.
The voltage sag event on phase B lasts ~35 ms as captured by the SEL 735 meter:
There is no active notification in Slack but a cleared notification is received which states the active alarm duration is 2ms:
When I search the time listed in the notification there is no correlating journal entry:
When I view the tag history there is no record of the Boolean tag going high:
I'm trying to understand how these events have slipped through and triggered notification. Any insight is greatly appreciated.