Hi there,
I have a tag browse tree where i want to select the tag and add/update desired "Notes"(Not the ack notes) in already existing alarm. I am trying to use system.tag.configure with system.tag.get configuration can anyone tell me what I am doing wrong.
This script is configured under a button action performed event.
def runAction(self, event):
tagPath = self.getSibling("TagBrowseTree").props.selection.values[0]
tagConfig = system.tag.getConfiguration(tagPath)
tagConfig[0]['alarms'][0]['Notes'] = self.getSibling("TextArea").props.text
system.tag.configure(tagPath, tagConfig, "o")
self.getSibling("Label_0").props.text= 'Notes Updated Successfully'
Patience is key, this is an international forum, and timezones change when large amounts of users are active. expecting an answer in 4 hours from a volunteer user base is pretty impatient.
That said, chuck in a logger and print the output of tagConfig just after you assign it, then do the same just after you have changed the notes.
Have a look and see if you are changing the correct pieces as intended.
Also check the log for errors when you run the action.
On top of that, check out the example in this link:
https://docs.inductiveautomation.com/display/DOC81/system.tag.configure
There is instruction that the input is a list of tags and the output also a list of tags, so perhaps you need to follow the examples and see how they send their tag paths to the functions.
Thanks for you quick response. I apologize and will work on my ability to wait patiently.
Really appreciate your help.
from com.inductiveautomation.ignition.common.tags.paths.parser import TagPathParser
path = tagPath
ParentPath = TagPathParser.parse(path)
system.tag.configure(ParentPath.parentPath, tagConfig, "o")
system.tag.configure needs a parent path I was initially using tag path.