Using Modbus Slaver software to test that communication is normal and why data cannot be displayed properly

step1:


step2:

step3:

step4:

You need to set the “One-based Addressing” setting to false for that device connection.

It also helps to start without the mapping. Just make an OPC tag in the designer with “[device]255.C0” or “[device]255.C1” as the OPC Item Path.