Hello,
I have a PLC from B&R Automation, which have an HMI installed near it. I’m trying to read a value (temperature_ from a register based on a list which I got from the guy who programmed the PLC.
The values that is read is not matching the value that is in local HMI. I tried different designators but nothing came close to that value. Is a problem of scaling this value?
Does anyone have an ideea in this case?
Thank you!!
REAL is a floating point. Did you try IRF?
1 Like
Hi. I tried IRF also, and I got this value:
I’m expecting something near STC 42 value below:
This register is for STC42.
Looks like a byte order problem. Try different values for byte/word swapping and/or zero-based addressing (in the device settings, not the prefix).
1 Like
Where I can do these settings? Ignition or the PLC?
Thanks!
In Ignition. In the device settings in the gateway.
1 Like
I had to uncheck this box.
Now it works.
Thanks for help!!