Vision Client is not communicatng with PLC;But able to communicate in quick client...when read the status is good

Vision Client is not communicatng with PLC;But able to communicate in quick client...when read the status is good

This typically happens when an OPC server is buggy. You can set up one or more dedicated tag groups that use OPC read instead of subscribe and place all of that server's tags in such a group.