What logic drives this.....[System]Gateway/Redundancy/Connection/IsConnected
Hi All,
What is the logic behind this tag going false?
This tag is going false once a day, trying to troubleshoot to identify cause.
the other related tags are true and do not go false like:
[System]Gateway/Redundancy/IsActive
Thank you in advance
It’s mostly driven by the gateway network connection state between the master and backup gateways. If the connection faults, this value will become false. There are other things that drive the value, like if the master and backup gateways are incompatible due to platform or installed module differences. But these wouldn’t cause the value to change once per day. The first place to troubleshoot would be the gateway network connection between the master and backup gateways.
Setup history on it so you can determine if it truly is only once a day, and if so, is it the same time every day? If so, is your IT dept doing something?
thank you, we’re investigating network connectivity
It is not unusual for network active security probes to disrupt comms in some environments.
Problem is resolved we upgraded to 8.1.53.