What Modbus register do I need to talk to a counter in iSMA-B-8I-IP?
Hello,
I have an iSMA-B-8I-IP with following registers:
I want to read one of the counters but am struggling with what designator I need to pick for it in the Ignition tag configuration.
ns=1;s=[iSMA_Modbus]HRI23
and
ns=1;s=[iSMA_Modbus]HRUI23
both fail. My connection in the gateway shows status of connected.
Any advice on what I should try is appreciated.
Try enabling Zero-based Addressing in the device connection configuration page.
Your device may also be one that requires a unit ID in front of the designator, so you could try ns=1;s=[iSMA_Modbus]1.HRI23 or ns=1;s=[iSMA_Modbus]255.HRI23 (1 and 255 are common device unit ID defaults, see if yours has a different default unit ID).
Yes, adding a unit ID of 1 to the start of it worked correctly.
ns=1;s=[iSMA_Modbus]1.HRUI23
Thank you!