Working on Omron Fins Driver
Hi, I’m working on a Fins driver. I’ve found a Python 3.0 driver for Omron Fins protocol. It works on python 3.0. However, I have Ignition v7.5.13 with python 2.5. The idea is to use a gateway script to read and write tags.
The script generates syntax error on line 14. How could I do this on python 2.5?
self.CIO_BIT=b’\x30’ # (not supported in python 2.5)
(I send the script as an attachment).
Fins.py (14.2 KB)
Hi! welcome to the forums! :slight_smile:
the binascii library may be what you are needing to assign a hex of integer literal:
ok, I've solved this part but now I get error with ABCMeta from ABC
I've tried :
from abc import ABCMeta, abstractmethod
and:
ABCMeta = type
def abstractmethod(func):
return fun
I get error In both cases
Here is my code: (I attach it too)
import binascii
ABCMeta = type
return func
class FinsPLCMemoryAreas:
def init(self):
#"""Hex code for memory areas
#Each memory area has a corresponding hex code for word access, bit access
#forced word access and forced bit access. This class provides name-based
#access to them.
self.CIO_BIT=binascii.hexlify('\x30')
self.WORK_BIT=binascii.hexlify('\x31')
self.HOLDING_BIT=binascii.hexlify('\x32')
self.AUXILIARY_BIT=binascii.hexlify('\x33')
self.CIO_BIT_FORCED=binascii.hexlify('\x70')
self.WORK_BIT_FORCED=binascii.hexlify('\x71')
self.HOLDING_BIT_FORCED=binascii.hexlify('\x72')
self.CIO_WORD=binascii.hexlify('\xB0')
self.WORK_WORD=binascii.hexlify('\xB1')
self.HOLDING_WORD=binascii.hexlify('\xB2')
self.AUXILIARY_WORD=binascii.hexlify('\xB3')
self.CIO_WORD_FORCED=binascii.hexlify('\xF0')
self.WORK_WORD_FORCED=binascii.hexlify('\xF1')
self.HOLDING_WORD_FORCED=binascii.hexlify('\xF2')
self.TIMER_FLAG=binascii.hexlify('\x09')
self.COUNTER_FLAG=binascii.hexlify('\x09')
self.TIMER_FLAG_FORCED=binascii.hexlify('\x49')
self.COUNTER_FLAG_FORCED=binascii.hexlify('\x49')
self.TIMER_WORD=binascii.hexlify('\x89')
self.COUNTER_WORD=binascii.hexlify('\x89')
self.DATA_MEMORY_BIT=binascii.hexlify('\x02')
self.DATA_MEMORY_WORD=binascii.hexlify('\x82')
self.EM0_BIT=binascii.hexlify('\x20')
self.EM1_BIT=binascii.hexlify('\x21')
self.EM2_BIT=binascii.hexlify('\x22')
self.EM3_BIT=binascii.hexlify('\x23')
self.EM4_BIT=binascii.hexlify('\x24')
self.EM5_BIT=binascii.hexlify('\x25')
self.EM6_BIT=binascii.hexlify('\x26')
self.EM7_BIT=binascii.hexlify('\x27')
self.EM8_BIT=binascii.hexlify('\x28')
self.EM9_BIT=binascii.hexlify('\x29')
self.EMA_BIT=binascii.hexlify('\x2A')
self.EMB_BIT=binascii.hexlify('\x2B')
self.EMC_BIT=binascii.hexlify('\x2C')
self.EMD_BIT=binascii.hexlify('\x2D')
self.EME_BIT=binascii.hexlify('\x2E')
self.EMF_BIT=binascii.hexlify('\x2F')
self.EM10_BIT=binascii.hexlify('\xE0')
self.EM11_BIT=binascii.hexlify('\xE1')
self.EM12_BIT=binascii.hexlify('\xE2')
self.EM13_BIT=binascii.hexlify('\xE3')
self.EM14_BIT=binascii.hexlify('\xE4')
self.EM15_BIT=binascii.hexlify('\xE5')
self.EM16_BIT=binascii.hexlify('\xE6')
self.EM17_BIT=binascii.hexlify('\xE7')
self.EM18_BIT=binascii.hexlify('\xE8')
self.EM0_WORD=binascii.hexlify('\xA0')
self.EM1_WORD=binascii.hexlify('\xA1')
self.EM2_WORD=binascii.hexlify('\xA2')
self.EM3_WORD=binascii.hexlify('\xA3')
self.EM4_WORD=binascii.hexlify('\xA4')
self.EM5_WORD=binascii.hexlify('\xA5')
self.EM6_WORD=binascii.hexlify('\xA6')
self.EM7_WORD=binascii.hexlify('\xA7')
self.EM8_WORD=binascii.hexlify('\xA8')
self.EM9_WORD=binascii.hexlify('\xA9')
self.EMA_WORD=binascii.hexlify('\xAA')
self.EMB_WORD=binascii.hexlify('\xAB')
self.EMC_WORD=binascii.hexlify('\xAC')
self.EMD_WORD=binascii.hexlify('\xAD')
self.EME_WORD=binascii.hexlify('\xAE')
self.EMF_WORD=binascii.hexlify('\xAF')
self.EM10_WORD=binascii.hexlify('\x60')
self.EM11_WORD=binascii.hexlify('\x61')
self.EM12_WORD=binascii.hexlify('\x62')
self.EM13_WORD=binascii.hexlify('\x63')
self.EM14_WORD=binascii.hexlify('\x64')
self.EM15_WORD=binascii.hexlify('\x65')
self.EM16_WORD=binascii.hexlify('\x66')
self.EM17_WORD=binascii.hexlify('\x67')
self.EM18_WORD=binascii.hexlify('\x68')
self.EM_CURR_BANK_BIT=binascii.hexlify('\x0A')
self.EM_CURR_BANK_WORD=binascii.hexlify('\x98')
self.EM_CURR_BANK_NUMBER=binascii.hexlify('\xBC')
self.TASK_FLAG_BIT=binascii.hexlify('\x06')
self.TASK_FLAG_STATUS=binascii.hexlify('\x46')
self.INDEX_REGISTER=binascii.hexlify('\xDC')
self.DATA_REGISTER=binascii.hexlify('\xBC')
self.CLOCK_PULSES=binascii.hexlify('\x07')
self.CONDITION_FLAGS=binascii.hexlify('\x07')
class FinsCommandCode:
def init(self):
"""Hex code for fins command code
    Each fins command has a corresponding hex code. This class provides name-based
    access to them.
    self.MEMORY_AREA_READ=binascii.hexlify('\x01\x01')
    self.MEMORY_AREA_WRITE=binascii.hexlify('\x01\x02')
    self.MEMORY_AREA_FILL=binascii.hexlify('\x01\x03')
    self.MULTIPLE_MEMORY_AREA_READ=binascii.hexlify('\x01\x04')
    self.MEMORY_AREA_TRANSFER=binascii.hexlify('\x01\x05')
    self.PARAMETER_AREA_READ=binascii.hexlify('\x02\x01')
    self.PARAMETER_AREA_WRITE=binascii.hexlify('\x02\x02')
    self.PARAMETER_AREA_FILL=binascii.hexlify('\x02\x03')
    self.PROGRAM_AREA_READ=binascii.hexlify('\x03\x06')
    self.PROGRAM_AREA_WRITE=binascii.hexlify('\x03\x07')
    self.PROGRAM_AREA_CLEAR=binascii.hexlify('\x03\x08')
    self.RUN=binascii.hexlify('\x04\x01')
    self.STOP=binascii.hexlify('\x04\x02')
    self.CPU_UNIT_DATA_READ=binascii.hexlify('\x05\x01')
    self.CONNECTION_DATA_READ=binascii.hexlify('\x05\x02')
    self.CPU_UNIT_STATUS_READ=binascii.hexlify('\x06\x01')
    self.CYCLE_TIME_READ=binascii.hexlify('\x06\x20')
    self.CLOCK_READ=binascii.hexlify('\x07\x01')
    self.CLOCK_WRITE=binascii.hexlify('\x07\x02')
    self.MESSAGE_READ=binascii.hexlify('\x09\x20')
    self.ACCESS_RIGHT_ACQUIRE=binascii.hexlify('\x0C\x01')
    self.ACCESS_RIGHT_FORCED_ACQUIRE=binascii.hexlify('\x0C\x02')
    self.ACCESS_RIGHT_RELEASE=binascii.hexlify('\x0C\x03')
    self.ERROR_CLEAR=binascii.hexlify('\x21\x01')
    self.ERROR_LOG_READ=binascii.hexlify('\x21\x02')
    self.ERROR_LOG_CLEAR=binascii.hexlify('\x21\x03')
    self.FINS_WRITE_ACCESS_LOG_READ=binascii.hexlify('\x21\x40')
    self.FINS_WRITE_ACCESS_LOG_CLEAR=binascii.hexlify('\x21\x41')
    self.FILE_NAME_READ=binascii.hexlify('\x22\x01')
    self.SINGLE_FILE_READ=binascii.hexlify('\x22\x02')
    self.SINGLE_FILE_WRITE=binascii.hexlify('\x22\x03')
    self.FILE_MEMORY_FORMAT=binascii.hexlify('\x22\x04')
    self.FILE_DELETE=binascii.hexlify('\x22\x05')
    self.FILE_COPY=binascii.hexlify('\x22\x07')
    self.FILE_NAME_CHANGE=binascii.hexlify('\x22\x08')
    self.MEMORY_AREA_FILE_TRANSFER=binascii.hexlify('\x22\x0A')
    self.PARAMETER_AREA_FILE_TRANSFER=binascii.hexlify('\x22\x0B')
    self.PROGRAM_AREA_FILE_TRANSFER=binascii.hexlify('\x22\x0C')
    self.DIRECTORY_CREATE_DELETE=binascii.hexlify('\x22\x15')
    self.MEMORY_CASSETTE_TRANSFER=binascii.hexlify('\x22\x20')
    self.FORCED_SET_RESET=binascii.hexlify('\x23\x01')
    self.FORCED_SET_RESET_CANCEL=binascii.hexlify('\x23\x02')
    self.CONVERT_TO_COMPOWAY_F_COMMAND=binascii.hexlify('\x28\x03')
    self.CONVERT_TO_MODBUS_RTU_COMMAND=binascii.hexlify('\x28\x04')
    self.CONVERT_TO_MODBUS_ASCII_COMMAND=binascii.hexlify('\x28\x05')
class FinsResponseEndCode:
def init(self):
self.NORMAL_COMPLETION=binascii.hexlify('\x00\x00')
self.SERVICE_CANCELLED=binascii.hexlify('\x00\x01')
#class FinsConnection(metaclass=ABCMeta):
class FinsConnection(metaclass):
def init(self):
self.dest_node_add=0
self.srce_node_add=0
self.dest_net_add=0
self.srce_net_add=0
self.dest_unit_add=0
self.srce_unit_add=0
@abstractmethod
def execute_fins_command_frame(self,fins_command_frame):
pass
def fins_command_frame(self,command_code,text=binascii.hexlify(''), service_id=binascii.hexlify('\x60'),
icf=binascii.hexlify('\x80'),gct=binascii.hexlify('\x07'),rsv=binascii.hexlify('\x00')):
command_bytes=icf+rsv+gct+
self.dest_net_add.to_bytes(1,'big')+self.dest_node_add.to_bytes(1,'big')+
self.dest_unit_add.to_bytes(1,'big')+self.srce_net_add.to_bytes(1,'big')+
self.srce_node_add.to_bytes(1,'big')+self.srce_unit_add.to_bytes(1,'big')+
service_id+command_code+text
return command_bytes
def plc_program_to_file(self,filename,number_of_read_bytes=992):
    """Read the program from the connected FINS device
    :param filename: Filename to write the program from the FINS device
    :param number_of_read_bytes: Bytes to read from the device per cycle(default 992)
    program_buffer=binascii.hexlify('')
    output_file=open(filename,'wb')
    done=False
    current_word=0
    while not done:
        response=self.program_area_read(current_word,number_of_read_bytes)
        #Strip FINS frame headers from response
        response=response[10:]
        #The MSB of the 10th Byte of response is the last word of data flag
        done = response[10]>0x80
        #Strip command information from response leaving only program data
        response=response[12:]
        program_buffer+=response
        current_word+=number_of_read_bytes
    output_file.write(program_buffer)
def file_to_plc_program(self,filename,number_of_write_bytes=992):
    """Write a stored hex program to the connected FINS device
    :param number_of_write_bytes: Bytes to write per cycle(default 992)
    input_file=open(filename,'rb')
    program_buffer+=input_file.read()
    if len(program_buffer)%number_of_write_bytes != 0:
        write_cycles = len(program_buffer)//992+1
    else:
    current_word=0
    #PLC must be in program mode to do a program area write
    self.change_to_program_mode()
    for i in range(write_cycles):
        number_of_write_bytes_with_completion_flag=number_of_write_bytes
        if i == write_cycles-1:
            number_of_write_bytes=len(program_buffer)%number_of_write_bytes
            number_of_write_bytes_with_completion_flag=number_of_write_bytes+0x8000
        current_data=program_buffer[current_word:current_word+number_of_write_bytes]
        self.program_area_write(current_word,number_of_write_bytes_with_completion_flag,current_data)
        current_word+=number_of_write_bytes
    #Change back to run mode after PLC program is written
    self.change_to_run_mode()
def memory_area_read(self,memory_area_code,beginning_address=binascii.hexlify('\x00\x00\x00'),number_of_items=1):
    """Function to read PLC memory areas
    :param memory_area_code: Memory area to read
    :param beginning_address: Beginning address
    :param number_of_items: Number of items to read
    :return: response
    assert len(beginning_address)==3
    data = memory_area_code+beginning_address+number_of_items.to_bytes(2,'big')
    response=self.execute_fins_command_frame(
        self.fins_command_frame(FinsCommandCode().MEMORY_AREA_READ,data))
    return response
def memory_area_write(self,memory_area_code,beginning_address=binascii.hexlify('\x00\x00\x00'), write_bytes=binascii.hexlify(''), number_of_items=0):
    """Function to write PLC memory areas
    :param memory_area_code: Memory area to write
    :param write_bytes: The bytes to write
    :return: response
    data = memory_area_code+beginning_address+number_of_items.to_bytes(2,'big')+write_bytes
        self.fins_command_frame(FinsCommandCode().MEMORY_AREA_WRITE,data))
    return response
def program_area_read(self,beginning_word,number_of_bytes=992):
    """Function to read PLC program area
    :param beginning_word: Word to start read
    :param number_of_bytes: Number of bytes to read
    :return: response
    program_number=binascii.hexlify('\xff\xff')
    data=program_number+beginning_word.to_bytes(4,'big')+number_of_bytes.to_bytes(2,'big')
        self.fins_command_frame(FinsCommandCode().PROGRAM_AREA_READ,data))
    return response
def program_area_write(self,beginning_word,number_of_bytes,program_data):
    """Function to write data to PLC program area
    :param beginning_word: Word to start write
    :param number_of_bytes: Number of bytes to write
    :param program_data: List with end code and response
    :return:
    data=program_number+beginning_word.to_bytes(4,'big')+number_of_bytes.to_bytes(2,'big')+program_data
        self.fins_command_frame(FinsCommandCode().PROGRAM_AREA_WRITE,data)
    return response
def cpu_unit_data_read(self,data=binascii.hexlify('')):
    """Function to read CPU unit data
    :param data:
    :return:
        self.fins_command_frame(FinsCommandCode().CPU_UNIT_DATA_READ,data)
    return response
def cpu_unit_status_read(self):
    """Function to read CPU unit status
    :return:
        self.fins_command_frame(FinsCommandCode().CPU_UNIT_STATUS_READ)
    return response
def change_to_run_mode(self):
    """Function to change PLC to run mode
    :return:
        self.fins_command_frame(FinsCommandCode().RUN)
    return response
def change_to_program_mode(self):
    """ Function to change PLC to program mode
    :return:
        self.fins_command_frame(FinsCommandCode().STOP)
    return response
udp
import socket
#from fins import FinsConnection
class UDPFinsConnection(FinsConnection):
def __init__(self):
    super().__init__()
    self.BUFFER_SIZE=4096
    self.fins_socket=socket.socket(socket.AF_INET,socket.SOCK_DGRAM)
    self.ip_address='10.162.92.30'
    self.fins_port=None
    """Sends FINS command using this connection
    Implements the abstract method required of FinsConnection
    :param fins_command_frame:
    :return: :raise:
    response = ""
    self.fins_socket.sendto(fins_command_frame,(self.ip_address,9600))
    try:
        response=self.fins_socket.recv(self.BUFFER_SIZE)
    except :
    # Exception as err:
        print(err)
    return response
def connect(self, IP_Address, Port=9600):
    """Establish a connection for FINS communications
    :param IP_Address: The IP address of the device you are connecting to
    :param Port: The port that the device and host should listen on (default 9600)
    self.fins_port=Port
    self.ip_address=IP_Address
    self.fins_socket.bind(('',Port))
    self.fins_socket.settimeout(1.0)
def __del__(self):
    self.fins_socket.close()
#Program: The following program read CIO 100 (0x1f) , and then write to tag 'test'
fins_instance = fins.udp.UDPFinsConnection()
fins_instance.connect('10.162.92.30')
fins_instance.dest_node_add=30
fins_instance.srce_node_add=238
mem_area = fins_instance.memory_area_read(fins.FinsPLCMemoryAreas().CIO_WORD,binascii.hexlify('\x00\x64\x00'))
system.tag.write('test',mem_area)
OmronFins.txt (15.9 KB)
Hi Bernardo,
When you post code on the forum, putting your code in blocks helps display the indentation properly.
I am so sorry. Write the post again
ok, I’ve solved this part but now I get error with ABCMeta from ABC
I’ve tried :
and:
ABCMeta = type
return fun
Here is my code:
import binascii
ABCMeta = type
	return func
    def __init__(self):
        #access to them.
    def __init__(self):
        access to them.
    def __init__(self):
    def __init__(self):
        self.dest_net_add=0
        self.srce_net_add=0
    @abstractmethod
        pass
        command_bytes=icf+rsv+gct+\
                      self.dest_net_add.to_bytes(1,'big')+self.dest_node_add.to_bytes(1,'big')+\
                      self.dest_unit_add.to_bytes(1,'big')+self.srce_net_add.to_bytes(1,'big')+\
                      self.srce_node_add.to_bytes(1,'big')+self.srce_unit_add.to_bytes(1,'big')+\
        done=False
        current_word=0
        while not done:
        else:
        current_word=0
        :return: response
        return response
        :return: response
        return response
        :return: response
        return response
        :return:
        return response
        :param data:
        :return:
        return response
        :return:
        return response
        :return:
        return response
        :return:
        return response
# udp
import socket
    def __init__(self):
        super().__init__()
        self.fins_port=None
        :return: :raise:
        response = ""
        try:
        except :
        # Exception as err:
            print(err)
        return response
        self.fins_port=Port
    def __del__(self):
I need to connect to several Omron CP1L devices that, according documentation, use the FINS protocol.
Can anyone offer information or advice?
Should I run to Kepware or Matrikon OPC to connect or are there better options?
I’d like to stay with Ignition as the only player if possible.
You’ll need to use Kepware unless you can wait until next year. Omron FINS is on the roadmap but we’re not doing any new drivers until Ignition 8.0 is released.
Thank you,
I’ll use a Kepware subscription license until drivers are available from IA.
What is that CIO 100 mean , does it is system generated memory address??
I want to read
BOOL 0.01 Filter Mode Select 0
BOOL W10.10 Enable Backwash Mode 0
BOOL W105.03 Polishing Tank Level Analog Sensor Fault 0
from an OMRON CP1L PLC, can you guide me how to do that??
It’s been over a year… any update on a driver for Omron FINS?
I have renewed Kepware licenses for another year at facilities that could not wait. We have more than a dozen facilities with Omron CJ devices anxiously waiting for a driver from IA. I won’t be able to delay much longer…
We’re working on it right now but I don’t have any idea when it will be released. The most likely would be with Ignition 8.1, but we’ll see.