Write a value to Master UDT Parameter
Hi All,
I am using Ignition Version 8.0.15.
I want to write a Value to a Master UDT parameter from a Tag.
Thanks in Advance,
Suresh
Hi.
Did you find a way to do it?
Thanks.
Hi Edward,
I have used the Tag Event Script to write the value to UDT parameter.
system.tag.write("[.]/Parameters.Value_Change", "5.5")
Thanks,
Suresh
Hi Suresh,
Thank you for the reply.
It seems like you're writing to an instance parameter. I'm actually trying to write to the data type parameter. I can do that, but I can't seem to get a value from it in the instance.
I'll keep hacking away at it :slight_smile:
Regards,
Ted.
Hi Ted,
system.tag.write("[.]/Parameters.Value_Change", "5.5"). This code I have written in the UDT Definition. The Value 5.5 varies for me instance to instance. So I use system.tag.write("[.]/Parameters.Value_Change", pvvalue)
Are you trying to push the value in UDT definition parameter and that reflects to all the instances? I hope I understand the requirement correctly.
If not, share some examples with screenshot, it will be helpful to understand.
Thanks,
Suresh
Hi Suresh,
Yes, I am, and its working. The only thing is the parameter values in the tag browser don't update for the instances.