I'm pretty new to ignition.
Looking to use an onClick event to write a value to a tag using a push button. Does the script below look correct or is there something that i'm missing. Thanks in Advance!
def runAction(self, event):
params = {
'deviceTagPath':[RiversideWTPProvider]HighService/HSP No1 Check Valve/OPEN,
'valueToWrite':1,}
I see the creation of a params dictionary and nothing else. So the dictionary will be created, then discarded at the end of the script. Your script should look more like:
system.tag.writeBlocking(['[RiversideWTPProvider]HighService/HSP No1 Check Valve/OPEN'], [1])
Note the placement of the tag path in a string, and both tagpath and value placed inside square brackets to make one-element lists of each. (See the docs for writeBlocking for why that is.)
Also, you should not use click events on buttons, as they don't respect the button's enabled/disabled state. Use the actionPerformed event instead.
Thank you for the insight!