Click PLC Communication with Ignition

Can you ping the CLICK from the Ignition gateway? Did you setup your addresses in the ModBus TCP? Note that you need to drop 0,1,3, or 4 from the beginning of your address that is handled when you select the register type -Connecting to Click PLC for tags?