Getting gateway loggers via script?
This is for 8.1 but curious about 8.3 too.
I would like to raise an alarm and warning inside 2 tags whenever the gateway logs have an error or warning occur, with some logic around clearing this out when no error/warnings over x time.
I'm wondering the best way to check the latest logs? I'm sure I remember a post showing how to get this through the gateway context, but haven't found it yet.
This may be what you were looking for:
…or at least a place to start.
(Found it! Thanks @tyler.bennett
Accessing Diagnostic Logs in Perspective - #6 by tyler.bennett)
@lane.duncan I had this prepped a while ago and was going to add to it where I ended up at, but got distracted working :sweat_smile: Thanks for your reply with it though. I will update this post shortly with the above
I ended up with this, where updateGatewayLogLevelCountTags() is called every minute from a GW timer script, and the Alarm Count tag has an alarm on it for value > 0
try:
	from com.inductiveautomation.ignition.gateway import IgnitionGateway
	from com.inductiveautomation.ignition.common.logging import LogQueryConfig
except: pass
def getGatewayLogLevelCounts(timePeriodMin=5, logRetrievalLimit=2000):
	'''Retrieves the count of each log level from the gateway logs for the last {timePeriodMin} minutes.
	Queries the gateway's internal log store (the same data backing the Status > Diagnostics > Logs
	page) via the unsupported/internal IgnitionGateway logging manager API, then tallies how many
	events fall into each standard log level.
	IMPORTANT: must run in the gateway context.
	Args:
		timePeriodMin (int): How many minutes back from now to query, e.g. 5 for the last 5 minutes.
		logRetrievalLimit (int): Max number of log events to pull from the query. Acts as a safety
			cap on a noisy window - if this limit is being hit regularly, counts will be
			undercounted and the limit should be raised.
	Returns:
		dict: Counts keyed by level name - {'ERROR': int, 'WARN': int, 'INFO': int, 'TRACE': int, 'DEBUG': int}.
	Raises:
		ValueError: If the gateway log query fails for any reason (e.g. not running in gateway
			scope, or the internal logging API is unavailable/changed).
	try:
		now = system.date.now()
		windowStart = system.date.addMinutes(now, -1 * timePeriodMin)
		startMillis = system.date.toMillis(windowStart)
		loggingManager = IgnitionGateway.get().getLoggingManager()
		queryBuilder = LogQueryConfig.newBuilder()
		queryBuilder.newerThan(startMillis)
		queryBuilder.limitTo(logRetrievalLimit)  # generous cap - raise if you're hitting the limit in a noisy 5min window
		logResults = loggingManager.queryLogEvents(queryBuilder.build())
		logEvents = logResults.getEvents()
		logLevelCounts = {'ERROR': 0, 'WARN': 0, 'INFO': 0, 'TRACE': 0, 'DEBUG': 0}
		for event in logEvents:
			level = str(event.getLevel()).upper()
			logLevelCounts[level] += 1
		return logLevelCounts
	except Exception, e:
		raise ValueError("Failed to query gateway logs and update alarm count tags: %s" % str(e))
def updateGatewayLogLevelCountTags():
	'''Updates the gateway alarm count tags with ERROR and WARN log counts from the last 5 minutes.
	Calls getGatewayLogLevelCounts() for a 5-minute window and writes the resulting ERROR and WARN
	counts to their respective alarm tags. Intended to be called on a recurring basis (e.g. from a
	1-minute Gateway Timer Event) so the tags stay current with a rolling 5-minute count, dropping
	back to 0 once no matching log events remain in the window.
	IMPORTANT: must run in the gateway context (see getGatewayLogLevelCounts).
	Tags written:
		[default]System/Alarms/Gateway Application Error Count
		[default]System/Alarms/Gateway Application Warn Count
	logLevelCounts = getGatewayLogLevelCounts(timePeriodMin=5)
	errorCount = logLevelCounts['ERROR']
	warnCount = logLevelCounts['WARN']
	errorTagPath = "[default]System/Alarms/Gateway Application Error Count"
	warnTagPath = "[default]System/Alarms/Gateway Application Warn Count"
	system.tag.writeBlocking([errorTagPath, warnTagPath], [errorCount, warnCount])