Hello All,
Wondering what others have used with success to communicate to Mitsubishi PLCs. Here is some equipment below I will need to communicate with.
R08CPU
RD81OPC96
Regards,
Frank
Hello All,
Wondering what others have used with success to communicate to Mitsubishi PLCs. Here is some equipment below I will need to communicate with.
R08CPU
RD81OPC96
Regards,
Frank
There is no built-in driver from IA for Mitsi. You will need to use KepServer etc as your OPC-UA server, and have Ignition connect to that.
IIRC from the ICC panel, a Mitsi driver is in the works.