Hello All,

Wondering what others have used with success to communicate to Mitsubishi PLCs. Here is some equipment below I will need to communicate with.

R08CPU
RD81OPC96

Regards,

Frank

There is no built-in driver from IA for Mitsi. You will need to use KepServer etc as your OPC-UA server, and have Ignition connect to that.

IIRC from the ICC panel, a Mitsi driver is in the works.