Installing Ignition Edge 8.0.3 on the same computer that has Ignition 8.0.3

Any tips on how to install Ignition Edge 8.0.3 on the same computer that has Ignition 8.0.3.

I am using a laptop with Windows 10 OS, running Ignition 8.0.3 normally.

I am not getting any error when installing Ignition Edge 8.0.3 on that same laptop. I shit down the Ignition software, Designer application & the gateway associated with it. But when I go to the webpage [http://localhost:8088/web/home?0 I do not see Ignition Edge.

Appreciate any help in resolving this.

Can you post the wrapper.log found in the logs directory of the Ignition Edge install directory?

ERROR | wrapperm | 2019/09/08 10:07:45 | The Ignition Gateway service is not installed - The specified service does not exist as an installed service. (0x424)
ERROR | wrapperm | 2019/09/09 05:50:34 | The Ignition Gateway service is already started with status: RUNNING
ERROR | wrapperm | 2019/09/09 06:08:56 | The Ignition Gateway service is already started with status: RUNNING
ERROR | wrapperm | 2019/09/09 13:36:30 | The Ignition Gateway service is already started with status: RUNNING
ERROR | wrapperm | 2019/09/09 13:44:44 | Unable to install the Ignition Gateway service - The specified service already exists. (0x431)
STATUS | wrapperm | 2019/09/09 13:44:53 | Starting the Ignition Gateway service…
INFO | wrapperm | 2019/09/09 13:44:59 | Waiting to start…
STATUS | wrapperm | 2019/09/09 13:45:01 | Ignition Gateway service started.
STATUS | wrapperm | 2019/09/09 13:46:32 | Stopping the Ignition Gateway service…
STATUS | wrapperm | 2019/09/09 13:46:37 | Ignition Gateway service stopped.

If you’re trying to have two gateways installed on the same machine, you’ll need to make sure they have different service names, otherwise you’ll see issues installing the service. In ignition.conf, there’s a property near the end of the file called wrapper.name - for the Edge install, you’ll want to change that to something other than Ignition so it doesn’t clash with the service name for the Ignition install. After making that change, you can properly install the service.

If you want the gateways to run at the same time, you’ll need to modify data/gateway.xml in the Edge install directory to use different ports than the Ignition install.

1 Like