Issues syncing Tag History from Ignition Edge to Standard Gateway (History Sync)
Hi everyone,
I'm having trouble synchronizing tag history from an Ignition Edge (v8.3.1) to a central Ignition Standard Gateway.
Current Architecture:
  • Edge Gateway: Has a local historian named edHistorian.
  • Standard Gateway (Name: igResidual): Has a Historian Splitter named pgHubSpoke (which points to a local SQL DB and a remote Hub).
  • The Gateway Network connection is established and "Running" between both nodes.
The Issue: I have configured the Edge Sync Settings to point to the Remote Gateway igResidual and the Remote History Provider pgHubSpoke. However, data is not flowing and I see the following symptoms:
  1. Logs in Edge: I see I/O exception (org.apache.http.NoHttpResponseException) when trying to reach the Standard Gateway on port 8060.
  2. Store & Forward: On the Edge side, I see many data points going into Quarantine.
  3. Logs mention: Historian syncable 'edHistorian' is starting. Will synchronize data to remote historian 'pgHubSpoke' on server 'igResidual'.
What I've checked so far:
  • The System Name of the Standard Gateway matches the "Remote Gateway Name" in Edge Sync Settings.
  • The provider name pgHubSpoke exists and is running on the Standard Gateway.
  • The Tag History module is running on both Gateways.
Questions:
  1. Are there specific Service Security settings in the Standard Gateway (under Gateway Network Services -> History Sync) that I should verify beyond setting the Access Level to "Allow All"?
  2. Does the fact that the remote provider is a Historian Splitter instead of a direct SQL Historian affect the Edge Sync capability?
  3. Why would I be getting NoHttpResponseException if the Gateway Network status shows as "Connected"?
Any advice on how to debug the quarantine or the connection would be greatly appreciated. Thanks!
That suggests that the gateway network is not set up correctly.
Also, is the central gateway also v8.3? If not, it won't work at all.
Yes, both Gateways are running in version 8.3
@bsantaella Did you find a resolution? asking because I am having similar issues.
While the root cause to your issue might not be related, everyone should upgrade beyond 8.3.1 before troubleshooting Edge historian sync issues.
Related post: