So I noticed that if we use more than like 2 days of data we get a message where the tags as pens show up saying there’s no trend data available. Is this a bug, I remember it used to work. We are on 8.1.12.Thx, jake
I’m experiencing something similar with v8.1.18, but it doesn’t matter whether I select a realtime range or historical range. One day it works, the next day it doesn’t. One minute it works, and hour later I get the same message. Nothing in the logs. Not database errors.
If anyone was able to find the cause of this issue I would appreciate you sharing, I am seeing this issue on an internal development gateway after updating to 8.1.19.
Thank you,
Nile
How have you configured the trend?
Good morning Hayden,
I am using the ‘Power Chart’ component in Perspective to choose the tags to display on the chart and I have been using the default configurations that the charts sets when you add a pen.
Is there some more specific information I can provide?
Anyone with inductive chime in yet?
Was anyone here able to figure this out? I am experiencing the same issue.
We were having an issue with the db not keeping up, I had to add:
rewriteBatchedStatements=true;
To the Extra Connection Properties in the connection to the db in the ignition gateway.
Once I remove the following configuration, it works:
"tagBrowserStartPath"
But I configured this property in another project without an issue.
If you open the view with the power chart and use the browser to add a tag you go through the designer while it's open and see the path and how it's formated. It will be like histprov:....
where exactly do i add this statement ? i am not able to find a match
- Config>Database>Database Connections
So in the Gateway WebUI go to the above and in Extra Connection Properties
zeroDateTimeBehavior=convertToNull;connectTimeout=120000;socketTimeout=120000;rewriteBatchedStatements=true;
Just add it to the end of whatever is already there like mine.
Do these settings apply to specifc vendor like mssql or are they vendor agnostic?
It probably depends on the db, I'm using mysql, well google hosted db mysql 5.7 to be specific.
Did this solution worked?
Hello, I changed sample mode of my tags from On Change to Periodic with Sample Rate of 1 second and it works now. ![]()
MySQL, Ignition 8.1.43.
Hi.
I had the same issue with "no trend data source available (bad_not_found)"on a power chart. My tag history was set up with "on change" and a min time between samples of 30sec. Data was being logged to SQL.
As soon as I changed the history settings to periodic and 1 sec, the issue was fixed. I immediately changed the history back to periodic and it has been working OK since then.
This behaviour seems a little unusual. Would anyone from ignition care to comment?
I was experiencing a similar issue but only for some trends.
I realized that the trends that were having this issue had chartZoomLevel set to a value other than 1. When I reset this to 1, the pens displayed fine.
I did a Google search and what Google said sounded reasonable: " At higher zoom levels, the chart needs to display a more detailed view of the data. If the data is not being loaded or interpolated properly at that level of detail, the trends may not appear or may be incomplete."
Saving all my trends with a chartZoomLevel = 1 fixed the inconsistency of my problem. But, still, if the user increased the zoom level while viewing say Trend X and then goes back to Trend Y, the pens for Trend Y still can display "No Trend Data Source Available" since Trend Y trends cannot be properly rendered at the new zoom level. Clicking the Reset Zoom Level fixes that.