Share CoDeSys DUT with OPC UA to Ignition 2
Hello everyone,
I have set an OPC connection between my WAGO PLC and Ignition.
But I can't get my arrays of DUT inn to ignition rigth.
It works if I make arrays of INT, or REAL
I found this on the forum
Kevin.Herron
Lead Software Engineer
Aug 2022
Last time this came up with support it turned out the OPC UA server in the Wago PLCs don’t support the DataTypeDictionary mechanism, only the newer DataTypeDefinition attribute introduced in OPC UA 1.04, and because of this Ignition’s client is currently unable to decode structured values from these servers.
I don’t have firsthand confirmation for any of this though. It was relayed from Wago support to customer to our support to me…
So then I wounder when Igntion will support the DataTypeDefinition attribute introduced in OPC UA 1.04
As it looks like this is the problem.
Yes, could be the issue. We won’t have updated OPC UA support, which includes the DataTypeDefinition, until late Q4 or Q1 next year.
Hello Kevin,
I am facing the same issue, i need to access DUT created in Codesys to Ignition, if this feature is still not there in ignition OPC UA, could you please suggest me with some other ways to do it. Thanks.
Are you using a Wago PLC specifically or some other Codesys server? Not all Codesys products lack support for the DataTypeDictionary.
I am not using any PLC here; I am just trying with Codesys v3 sp21 soft PLC (CODESYS control for Linux Runtime L)