Nightly 8.1 Changelogs - 2022
Nightly Changelog: 8.1.18-b20220524
Perspective
3351: File Upload: Implement clearUploads() component method
Added clearUploads() script function to the FileUpload Component.
Platform
5392: Add formatting pattern / replacement tokens for manual and scheduled backup filename generation
Scheduled backups (as well as manually downloaded backups) now feature a customizable filename pattern with optional placeholders such as ${os}, ${version}, ${gatewayName}, ${edition} and ${timestamp}.
Nightly Changelog: 8.1.18-b20220525
Connectivity
5235: BACnet "readRaw" and "writeRaw" scripting functions
Added the system.bacnet.readRaw and system.bacnet.writeRaw scripting functions which allows any object/property combination to be read/written. Because the functions accept and return types used by the underlying BACnet4j library instead of translating to OPC UA and into types supported by tags, it serves as an escape hatch for objects not explicitly supported by the BACnet driver.
Weekly Changelog: 8.1.18-b20220526
Visualization
1920: SQL Update script settings on Button Disappear After Saving
Fixed an issue where the 'SQL Update' script builder would appear to lose its context when re-opened.
3208: Find/Replace IllegalArgumentExceptions are thrown unhandled to the EDT
Fixed an issue in Designer where some Find/Replace operations that result in an error would silently emit to the Console instead of presenting an error dialog window.
Connectivity
5963: Browsing and subscribing to tags via OPC-UA against an exposed remote tag provider takes too long
Improved performance of Exposed Tags, especially when subscribing to tags from a remote gateway.
Data Model
5182: Quick Blocking writes to Derived tags using JSON are not always completing
Improved to help ensure the OPC Tag has the most current value from source.
5971: Upgrade twilio-sdk dependency to 7.55.3 due to transitive dependency CVEs
Upgraded Twilio SDK dependency from 7.35.0 to 7.55.3.
Weekly Changelog: 8.1.18-b20220527
Visualization
2090: Perspective Split Container
The split container has been added to the list of Perspective components along with two component events: minBoundReached and maxBoundReached.
See Forum Post
5373: Translatable Terms via Component Translation will only allow one Term to be saved and remove any existing terms if adding a new one
Fixed a regression with component level translations being lost on Vision components.
Data Model
6118: Unable to edit parameters of remote tag provider UDTs that aren't on 8.1.17+
The Designer tag editor now properly shows the UDT Parameters category for remote Gateways using older versions.
5476: Power Chart: Annotations don't store to the annotations table when using a Tag History Splitter
Tag history splitter does not support storage of historical annotations.
Weekly Changelog: 8.1.19-b20220531
Visualization
4028: The designer's "Resource Notes" panel deviates from standard design, is not universally applicable
Expanded the concept of 'resource documentation' to apply to all resources. Right click any resource in the project browse tree to edit the documentation describing that resource.
Note: Named query and report resources had a unique documentation field previously. This documentation will be upgraded to the new style once the resource is opened and saved in the designer.
Weekly Changelog: 8.1.19-b20220602
Connectivity
5958: NPE in Discovery Wizard when server returns null discovery URL array
Fixed an NPE in discovery wizard when server returns a null discovery URL array.
Platform
5462: Disable HTML escaping in ThreadDumpUtil's GSON instance
Ignition file-based or console-based thread dumps now pretty print HTML characters, so word strings such as ''\u003cinit\u003e" in the dump are now formatted as .
Weekly Changelog: 8.1.19-b20220606
Infrastructure
3085: Allow Launchers to use OS Trust Store
Support for OS Trust Stores were added to Designer Launcher, Vision Client Launcher, Designers, Vision Clients, and Perspective Workstation. The trust.store property in each launchers config JSON now has three options:
trust.store value Windows Mac OS Linux
system Windows-ROOT KeychainStore ca-certificates
user Windows-MY KeychainStore ca-certificates
jvm Java internal cacerts Java internal cacerts Java internal cacerts
jvm is the default and matches the existing behaviors of the launchers which support certificate imports from within the application. The other OS trust store types map to their named Java Trust Store implementations with the exception of ca-certificates.
ca-certificates loads PEM bundles or certificate directories as defined by the ca-certificates package available for most linux distros. this option also supports two additional system properties to define either:
  • openSSL compliant certificate directory: ignition.net.ssl.certDir
  • PEM bundle: ignition.net.ssl.pemBundle
These OS trust stores will be used by running Designers, Clients, and Workstation once launched, but all types which are not jvm require launching clients and designers against gateways which include support for these trust store types. Retargets also conform to this requirement.
Visualization
994: Add "system.perspective.alterDock" scripting function to make dock configuration dynamic
New alterDock(dockId, config) scripting method, and complimentary Alter Dock action event. Alter the configuration of a dock on the fly by supplying the dock's ID and the desired configuration. See the alterDock scripting method's intelligent hint, or the Alter Dock action's documentation for more details.
Weekly Changelog: 8.1.19-b20220608
Security
6146 Ignition's Web Server's Default Error Handler returns "Caused By" line revealing Java Exception Message Details
Detailed server information is no longer leaked by Ignition's web server when an unhandled exception is thrown while handling HTTP requests.
Weekly Changelog: 8.1.19-b20220609
Visualization
2865: Translation Manager save working incorrectly when filter is applied
Fixed an issue with the translation manager in the designer not correctly loading translations when a search filter was applied.
Data Model
6086: Saving Internal Historian with Remote Sync Enabled while GAN connection is disabled causes duplicate data to be sent when GAN connection is re-enabled
Fixed an issue where the internal historian sync wouldn't properly deregister if interrupted while executing.
Weekly Changelog: 8.1.19-b20220611
Visualization
1733: Report module simple table 'overflow behavior' property is not working
Removed unused Paginate option for the Reporting Simple Table.
Weekly Changelog: 8.1.19-b20220613
Connectivity
5829: In OPC-DA connections, NPE in ComUtil#getValueForVariant method
Fixed an issue where OPC-DA subscriptions containing tags with unknown/unsupported data types causes other tags to stop updating.
6004: Logix devices unable to connect to backup GW when Standby Activity Level is set to β€˜Warm’ and the master GW is active
Fixed a bug which prevented Logix devices from connecting in certain situations while the gateway had a warm activity level.
Visualization
846: Totals on report duplicate a value intermittently depending on where page ends
Fixed Reporting summary row totals for table groupings from contributing to the grand total more than once when multiple pages are involved.
4671: Erroneous "Component name 'null' is invalid" error thrown on Vision clients accessed via thin client
Fixed an issue in the look-and-feel that would cause erroneous "Component name 'null' is invalid" errors in Vision clients and Designer sessions in certain RDP scenarios.
Security
4316: Password Reset Page can be used as an Oracle by attackers
Improved security of password reset page.
Data Model
6091: Transaction Group: DB to OPC mode value not scaling
Transaction group bidirectional OPC to database items now "de-scale" a scaled value when writing an updated database field value to the OPC tag.
Weekly Changelog: 8.1.19-b20220614
Visualization
784: Tree View component's Default Node Selected Background property not working in Ignition 8
Fixed some issues with tree view rendering. Also added two new properties to the tree view component: selectionFillColor, to change the full width selection highlight color, and fullWidthSelection, a boolean allowing you to disable the full width selection highlight entirely.
3787: LaF issue: Vision Progress Bar will always show a border regardless of Border prop setting
Fixed an issue with the Look-and-Feel causing the 'progress bar' component to always have a visible border.
6160: Vision Windows, a new feature to disable the root containers context menu
Removed a superfluous context menu that was showing up on containers with no other mouse event handlers in place.
2144: Report Parameters should default to default tag provider if one is not specified
Reimplemented default project provider evaluation for Reporting parameters when referencing tag paths.
1912: Backup failover notification can't be dismissed
Backup failover notification can now be dismissed.
Infrastructure
6122: Project Shortcut fails to launch due to large Description Length
Shortcuts created by the launchers on Windows now automatically truncate the description field to prevent launch issues.
Weekly Changelog: 8.1.19-b20220615
Data Model
6140: Service Security for MQTT providers' Tag Access reverts to 'Inherited' on Gateway Restart
Fixed issue where service security policies wouldn't refresh with the correct access levels when loading managed tag providers.
Visualization
4964: Redirect /web/workstation to /web/perspective-workstation
The /web/workstation route now redirects to /web/perspective-workstation.
1282: Increase Size of Security Level Permissions Text Input
Security level permissions text inputs are now resizable text areas.
Platform
6197: Folders in the data/modules don't get copied over from backup on Gateway restore
Cirrus Link module data is now restored from a gateway backup.
Weekly Changelog: 8.1.19-b20220616
Enterprise
4433: Add Retention Policy to EAM Collect Backup Task
EAM Controller now implements an optional maximum retention policy for agent gateway backups. Older gateway backups will be automatically deleted when the max retention age is exceeded. A maximum number of retained gateway backups can also be specified.
Visualization
3264: Unable to apply certain text style properties to the selected value of a perspective dropdown component
Dropdown Component - Added textAlign prop, it aligns the value(s) and/or placeholder text displayed within the dropdown. Valid values are 'left', 'center', and 'right'. textAlign within the dropdown modal itself may be overriden/set separately using props.dropdownOptionStyle.textAlign.
Weekly Changelog: 8.1.19-b20220620
Data Model
6217: Uncaught exception thrown when querying remote alarm journal in 8.1.18-rc1
Fixed uncaught exception when querying alarm journal through remote journal profile targeting gateway with version prior to 8.1.18.
Infrastructure
6159: Upgrade the launchers to javaFX 17
The Designer Launcher, Vision Client Launcher, and Perspective Workstation now use JavaFX 17.0.2
Enterprise
2393: Tag values not synchronizing correctly after comms were lost between redundant master and backup
After redundant master and backup lose contact with each other and both go active, the backup will now check if it has conflicting sync data as compared to the master. If it does, it will drop its own data in preference of the master's data.
Platform
584: Throw bespoke error message if message handler cannot be executed due to inheritable project
Now throwing a more specific error message when a message handler is called on an inheritable project (which can't run message handlers).
Visualization
2437: Add scary warning when trying to change a gateway name
Changing the gateway name now displays a warning modal, which requires confirmation before the change can be made.
Weekly Changelog: 8.1.19-b20220621
Visualization
5882: Tag Browse Tree - Shows a perpetual loading state if the project does not have a default tag provider specified
Perspective Tag Browse Tree component will now correctly display "no results found" if a default tag provider and a root path are not set.
4434: Button: The "align" component property doesn't work when button is in flex container in jxbrowser
Fixes an issue where the align property, in a flex container, would not properly align in the designer, but would function in a session.
Weekly Changelog: 8.1.19-b20220622
Data Model
6111: Improve Robustness of Transaction groups so that manual row insertions don't delete Data
Transaction groups now calculate old rows to be deleted by timestamp instead of id. The delete settings can now be modified to calculate old records by either gateway local time or database local time.
6117: Error publishing tag change event caused by attempt to nest TagValues
Prevent exception when subscribing to tags from 7.9 remote tag provider.
3789: Cosmetic: In alarm pipeline notification block, Roster Type drop down has blank description boxes
Added Tooltip descriptions on each Dropdown option for Pipeline Notification Block's Roster Types.
2063: Internal alarm journal, audit profile, and tag historian "drop" all records when renamed
Internal alarm journal. audit profile, and historian data will now persist when the configuration record (i.e. provider / profile) is renamed, resulting in renaming of the local SQLite database file.
6198: Remove ability to Bind Parent Data Type on UDT Definitions/Instances
Removed binding option from the UDT "parent data type" property within the tag editor.
Visualization
6090: Multiple popups will unmount when changing the stacking context on focus
Fixed issue with popups unmounting views when the stacking context of multiple popups changes.
Weekly Changelog: 8.1.19-b20220623
Visualization
5931: RunScript expression that calls custom method on template causes GUI thread to hang when loading
Fixed a significant performance regression in Vision template initialization.
5780: Perspective front-end should log information about why the websocket was closed
Adds websocket disconnect events to client side logs. Also alters client and server websocket disconnect logs with disconnect code information.
Weekly Changelog: 8.1.19-b20220624
Visualization
5266: Remove the "Procedures" tab on the Report "Add new object" window
Removed procedures tab
6137: Upgrade Vision Client Launcher imageio lib version due to CVE
Updated the imageio dependency used in the Vision Client Launcher to fix a CVE.
Weekly Changelog: 8.1.19-b20220627
Visualization
3993:Remove redundant config links on Edge config overview page
Redundant config links on edge config overview page have been removed.
2407: Fix potential NPE in RMKey.KeyAccessor.set() in reporting-common
Modified the loggers for Reporting key errors to be less frequent.
2280: File Upload and Icon components become unusable in Flex Container when not using stretch, cross browser and designer behavior inconsistent
The following Perspective Components will no longer have 0 width then they are the child of a Flex Container with props.alignItems not equal to stretch: Cylindrical Tank, File Upload, Flex Repeater, Icon, Image, Map, Moving Analog Indicator, LED Display, Progress Bar, Slider, Sparkline, Table, Thermometer, Embedded View, and View Canvas. In addition the sizing of SVG based components when in a Flex Container will be more consistent between Design and Preview modes in the Designer, and between supported browsers in the Client.
6143: Ignore Bad Quality Option Missing on Tag History Bindings in Perspective
Fixed missing Ignore Bad Quality option on Tag History Bindings in Perspective.